Old 07-19-2023, 05:42 PM
John V. John V. is offline
Ultimate Warrior
 
Join Date: Sep 2005
Posts: 4,747
Default

Nevermind. The capacitor tested right on the money (69/5).

Thought about all the reasons the contactor might not pull in and realized could be a Low Pressure Switch or the High Pressure Switch which has a reset button. Bent down and pushed in the reset and it clicked!

Put the capacitor back in, installed the disconnect, turned on the thermostat and it is running/cooling normally.

Obviously it tripped for a reason but I suspect the condenser coil needs a good cleaning and the dirty coil likely caused the trip.

Until further notice I'm sticking with that assumption. I'll give it a good bath in the near future, hopefully it will be fine until I can get back to it.