Default Do I still need a relay when using a thermal switch?

I am using this thermal switch for a fan on one of my fluid coolers: https://www.improvedracing.com/therm...00f-p-831.html


I'm so used to wiring up relays w/fuses to control electric fans (like for coolant radiators that draw 20+ amps), I didn't think that perhaps in the case of this thermal switch, that I may not need it.


The fan I'm controlling only draws 7.2 amps, that switch is rated for 10 amps.


Does this mean I don't need the relay in this case? I have a 25 amp continuous relay with a 30 amp fuse on hand, but if I can simplify my wiring, I'd like to. But on the other hand, if using a relay will make the strain easier on my electrical when it kicks on, then I'd rather go that route.


Thanks!

__________________
1969 Pontiac Firebird

Last edited by 92GTA; 05-21-2020 at 12:57 PM.
  #2  
Old 05-21-2020, 05:36 PM
johnta1's Avatar
johnta1 johnta1 is offline
Ultimate Warrior
 
Join Date: Feb 2001
Location: now sunny Florida!
Posts: 21,237
Default

Use the thermal switch as the switch to turn the fan relay on.
You need the main power to go to the fan from the relay.



__________________
John Wallace - johnta1
Pontiac Power RULES !!!
www.wallaceracing.com

Winner of Top Class at Pontiac Nationals, 2004 Cordova
Winner of Quick 16 At Ames 2004 Pontiac Tripower Nats

KRE's MR-1 - 1st 5 second Pontiac block ever!


"Every man has a right to his own opinion, but no man has a right to be wrong in his facts."

"People demand freedom of speech to make up for the freedom of thought which they avoid." – Socrates
  #3  
Old 05-21-2020, 05:37 PM
92GTA's Avatar
92GTA 92GTA is offline
Ultimate Warrior
 
Join Date: Aug 2016
Posts: 1,068
Default

So wire it as normal with a relay. Understood.

Thanks!

__________________
1969 Pontiac Firebird
  #4  
Old 05-22-2020, 05:38 AM
Geoff Geoff is offline
Ultimate Warrior
 
Join Date: Jul 2005
Location: Australia
Posts: 2,470
Default

You don't need a relay. The current capability of the switch is higher than the load, so safe to use the sw without a relay.

  #5  
Old 05-22-2020, 07:57 AM
"QUICK-SILVER" "QUICK-SILVER" is offline
Ultimate Warrior
 
Join Date: Feb 2008
Location: LaFayette Georgia
Posts: 5,512
Default

Quote:
Originally Posted by Geoff View Post
You don't need a relay. The current capability of the switch is higher than the load, so safe to use the sw without a relay.
The OP didn't post fan start-up amps.

Relays are cheap and easy to replace when their contacts get used up.

Clay

  #6  
Old 05-22-2020, 09:04 AM
Paul E Paul E is offline
Senior Chief
 
Join Date: Oct 2003
Location: Oshkosh WI
Posts: 311
Default

Quote:
Originally Posted by "QUICK-SILVER" View Post
The OP didn't post fan start-up amps.

Relays are cheap and easy to replace when their contacts get used up.

Clay

Yes this is correct


Sent from my iPhone using Tapatalk

  #7  
Old 05-22-2020, 12:08 PM
92GTA's Avatar
92GTA 92GTA is offline
Ultimate Warrior
 
Join Date: Aug 2016
Posts: 1,068
Default

Quote:
Originally Posted by "QUICK-SILVER" View Post
The OP didn't post fan start-up amps.

Derale doesn't publish those in their specs so I have no clue.



Better safe than sorry then with the relay.

__________________
1969 Pontiac Firebird
  #8  
Old 05-22-2020, 12:28 PM
Paul E Paul E is offline
Senior Chief
 
Join Date: Oct 2003
Location: Oshkosh WI
Posts: 311
Default

You said you already have a relay check around as there are many ways to mount the relay individually or in a multi relay mounted application. I did this in my 70 Lemans and mounted the unit in the inner fender behind the battery. Very easy to get to and I really removed all electrical draw from the original harness to the relay box for the horn hi and low beam, AC compressor clutch, coil, starter solenoid and blower fan. I am really happy with it. It did take some time and a lot of thought and layout. I purchased the wire termination ends so I could cut the wires to the correct length and terminate them instead of multiple splices. Is it over kill? YES it is!
Good luck.
Attached Thumbnails
Click image for larger version

Name:	relay box 1.jpg
Views:	104
Size:	66.7 KB
ID:	540739   Click image for larger version

Name:	relay box 4.jpg
Views:	106
Size:	51.4 KB
ID:	540740   Click image for larger version

Name:	relay wiring.jpg
Views:	108
Size:	97.6 KB
ID:	540741  

  #9  
Old 05-22-2020, 12:31 PM
92GTA's Avatar
92GTA 92GTA is offline
Ultimate Warrior
 
Join Date: Aug 2016
Posts: 1,068
Default

Nice. I have all of mine attached to the top of my radiator support facing forward. Hidden and easy to get to by just removing that 1 metal closeout panel. I also have a dedicated body ground going to the radiator support for that reason.

__________________
1969 Pontiac Firebird
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 09:59 AM.

 

About Us

The PY Online Forums is the largest online gathering of Pontiac enthusiasts anywhere in the world. Founded in 1991, it was also the first online forum for people to gather and talk about their Pontiacs. Since then, it has become the mecca of Pontiac technical data and knowledge that no other place can surpass.

 




Copyright © 2017