Default Not evacuating system

What would be the end result if you did not evacuate the a/c system before refilling it after it was all apart? Thanks

__________________
1974 Grand Prix Model J
  #2  
Old 07-11-2009, 12:16 PM
george kujanski's Avatar
george kujanski george kujanski is offline
Ultimate Warrior
 
Join Date: Jan 2000
Location: palatine, il. USA
Posts: 7,852
Default

It wouldn't work. First of all, getting enuf R-whatever into the system to allow the pressure switches to get the compressor to run is problematic. Secondly the moisture in the air in the system could freeze up inside, not allowing the refridgerant to flow, IIRC.

Getting the air and stuff out allows just refridgerant and oil to be in the system..that's what it's designed for.

George

__________________
"...out to my ol'55, I pulled away slowly, feeling so holy, god knows i was feeling alive"....written by Tom Wait from the Eagles' Live From The Forum
  #3  
Old 07-11-2009, 12:22 PM
johnsma22's Avatar
johnsma22 johnsma22 is offline
Ultimate Warrior
 
Join Date: Jun 2005
Location: Taunton, Ma
Posts: 1,928
Default

Short answer? It's NOT an option to not evacuate a refrigerant system into a deep vacuum (less than 500 microns) before charging. Your system will not work if the air and moisture are not removed before charging with refrigerant. Longer answer? Air is a non-condensable, meaning that it will not be condensed in the condenser, but rather, it will take up space and cause your system pressures to be too high to properly absorb and reject heat. Moisture in the air will also cause a lot of problems as it reacts with the refrigerant and oil.

__________________
John



"There are no stupid questions, but there are a LOT of inquisitive idiots!"
  #4  
Old 07-11-2009, 01:10 PM
77GP's Avatar
77GP 77GP is offline
Senior Chief
 
Join Date: Oct 2002
Location: Anderson, In
Posts: 349
Default

Well an idiot I guess told me that I didnt have to. We put the freon in and it did work idling to about 64F then eventually was 100F. That could possibly be the cause. We have installed new Expansion valve, lines, POA vlave and a condensor. Replaced all O-rings. All the lines were cold that were supposed to be then were very hot. Long story short-It has an appointment at a shop Monday morning. Leave it to the pros. Do you think it was freezing up due to all the air and moisture?? Thanks

__________________
1974 Grand Prix Model J
  #5  
Old 07-11-2009, 02:28 PM
Ben M.'s Avatar
Ben M. Ben M. is offline
Ultimate Warrior
 
Join Date: Jan 2004
Posts: 2,796
Default

Yes. Don't evacuate it to get it all out, how will you even know if it holds vacuum? It could have leaked all right out in 5 minutes.

  #6  
Old 07-11-2009, 03:03 PM
johnsma22's Avatar
johnsma22 johnsma22 is offline
Ultimate Warrior
 
Join Date: Jun 2005
Location: Taunton, Ma
Posts: 1,928
Default

Make sure you tell the guys at the shop that it's full of air before you let them hook their recovery equipment to it! When you asked this question I wish you had said that you had already done this and was planning on running the system. I would have told you not to start it! As you witnessed, air gets hot when it's compressed! I hope you didn't damage the compressor, because the pressures were probably through the roof!

They will have to blow the charge and not recover it as the air in your system could possibly damage their recovery unit. Once the system is pulled down into a vacuum, they should break the vacuum with nitrogen and pressurize the system to leak check it. You should also change the drier, as it was exposed to moisture laden air.

Once they are sure that the system is tight they will pull it down into a deep vacuum again and weigh in the system charge.

__________________
John



"There are no stupid questions, but there are a LOT of inquisitive idiots!"
  #7  
Old 07-11-2009, 03:14 PM
johnsma22's Avatar
johnsma22 johnsma22 is offline
Ultimate Warrior
 
Join Date: Jun 2005
Location: Taunton, Ma
Posts: 1,928
Default

Quote:
Originally Posted by 77GP View Post
Well an idiot I guess told me that I didnt have to.
This is only the case if leak repairs are made without needing to remove the refrigerant to make the repair and the system wasn't completely flat. Meaning that there still was some refrigerant pressure left in the system. Any pressure in the system means that air can't get in, only refrigerant leaking out. A system that has been opened to the atmosphere MUST ALWAYS be evacuated!

Once the repair is made the system is "topped off". I still don't like this method as you can't be sure how much refrigerant remained before you topped off. I like to start with an empty, evacuated system and weigh in the nameplate charge on critically charged systems. Critically charged means a system that doesn't have TXV (thermostatic expansion valve), but rather a fixed orifice or capillary tube. These systems require the "exact" amount of charge listed on the nameplate. TXV systems can be charged using the sub cooling method. This meaning that you add refrigerant until you get the correct condensed liquid line temperature for the given refrigerant.

__________________
John



"There are no stupid questions, but there are a LOT of inquisitive idiots!"
  #8  
Old 07-11-2009, 04:30 PM
77GP's Avatar
77GP 77GP is offline
Senior Chief
 
Join Date: Oct 2002
Location: Anderson, In
Posts: 349
Default

John,
Seems you are very knowlegeable about this. Thanks for the info and I will make sure they know what we have done.

__________________
1974 Grand Prix Model J
  #9  
Old 07-16-2009, 11:52 AM
78w72 78w72 is offline
Ultimate Warrior
 
Join Date: Nov 2007
Location: iowa
Posts: 4,747
Default

fwiw.....i have a 97 jeep 4.0 & the compressor bearing went bad on me. i bought a used replacement & hooked it back up without charging it. then, over a year later decided to buy a couple bottles of r134 & put them in without evacuating the system....it works great! blows ice coold & has worked for 2 years now with no problems at all.....

guess i was lucky

Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 03:08 PM.

 

About Us

The PY Online Forums is the largest online gathering of Pontiac enthusiasts anywhere in the world. Founded in 1991, it was also the first online forum for people to gather and talk about their Pontiacs. Since then, it has become the mecca of Pontiac technical data and knowledge that no other place can surpass.

 




Copyright © 2017